Short #85 - Low Voltage, Low Voltage
About this episode
In this short podcast episode, Bryan explains what happens when your low-voltage circuit puts out a lower voltage than it should.
Bryan recently received an email asking about the low voltage on a 20-ton split system with a long control wire; the voltage coming back to the condenser is only 19 volts, so there was some contactor chattering. First, in a case like that, you'll want to figure out why the voltage isn't as high as it should be. The control wire and line sets could be longer than the design specs, which may contribute to the problem. If the distance between components is the main issue, then you can use a relay to mitigate voltage drop and amp draw.
You'll also want to check that you've tapped the transformer correctly. Since most transformers are single-phase, they'll probably start off tapped to 240v; when you're dealing with three-phase equipment, you must ensure that the transformer is tapped to 208v.
One of the obvious issues to check is the voltage drop. If 26 volts are coming out of the transformer but you're only measuring 19, then you're clearly losing volts and have some resistance. Think about ALL of the conductors; is the drop the same across all of them? If so, then you've likely got a length and wire sizing problem. You can correct that issue with proper wire sizing; you can't always control the length, but if you can, then it's a good issue to address. If there's an issue with only one conductor, then the switch could have a problem, or there might be some wire splices.
If the load is drawing higher current than it should, then something could be impeding the motion on the solenoid, contactor, or another electrical component.
Learn more about Refrigeration Technologies HERE.
If you have an iPhone, subscribe to the podcast HERE, and if you have an Android phone, subscribe HERE.
More from HVAC School - For Techs, By Techs
Relative humidity is the number most technicians and homeowners know, but it can mislead. In this symposium session, Tim De Stasio and Sophie Ashley make the case that HVAC professionals should think…
In this short podcast episode, Bryan talks about why you're not done with a furnace service call or installation just because it lit. Ignition is just one part of the furnace sequence of operations, a…
In this session from the 2026 HVACR Training Symposium, Jim Fultz walks through his HVAC 101 class to help techs get through any gas furnace call. Jim's core message is to start with your senses, not…
In this short podcast episode, Bryan explains why every HVAC company needs a home performance contractor (or at least access to the skills provided by home performance contractors). Many people try to…
Heat pumps may be everywhere, but according to David Richardson, the industry is in danger of aiming at the wrong target. In this 2026 HVACR Training Symposium session, the Kentucky contractor's son,…